Old 02-04-2013, 11:58 PM   #1
New Camper
 
Join Date: Feb 2013
Location: Lutz, FL
Posts: 6


The air flow out of the 4 floor vents is hardly noticeable. The heat is barely perceptable.
What can I do to get some heat?

What I've done:
1. put covers over the center two vents...very little improvement in volume, and no improvement in heat.
2. checked heat coming out of exhaust. I can put my hand within 3-4 inches and not get burned.
3. using a mirror can tell there are no restrictions in the floor ducting.
4.put blocking at front and rear floor duct.
5. checked fan and it is running fine and making normal volume of noise for a furnace.
6.furnace ran all night with low of 34 degrees outside without shutting off or maintaining 72 degrees inside
7.this is my first outing with this unit and maybe this is all I get!?!?

Furnace unit is an Atwood 8525 and appears to be in good condition.
Is the low air volume normal?
Do I need to takeunit out and apart to verify burner.
Is this unit too small? Do I need a different brand furnace?

Looking for advice and input from others with this same TT.

y2kvette is offline   Reply With Quote
Old 02-05-2013, 12:14 AM   #2
Full Time Camper
 
tator447's Avatar
 
Join Date: Nov 2011
Location: WI
Posts: 896
Send a message via MSN to tator447


I'm not really versed in the furnace and I'm sure others will chime in...but my first thought goes to the LP and how much pressure you're getting. I'm sure they can get plugged or run sluggishly at times. Think about checking that out?

Good luck,
Jim
__________________

Jim & Linda Tator
Watertown, WI
2013 Crusier CF34SS GMC 3500 8.1L Dually
154 nights in 2013 - 4,370 miles
178 nights in 2014 - 5,082 miles
365 nights in 2015 - 6,040 miles
tator447 is offline   Reply With Quote
Old 02-05-2013, 12:31 AM   #3
Full Time Camper
 
Join Date: Nov 2006
Location: Bradley, Il
Posts: 1,018


Check the furnace for any blank covers having come off. Make sure all duct connections to furnace are tight. Check blower and blower compartment for blockage.
__________________
Dale & Carol
Bradley, Il
2007 F-250
2010 CF30SK Patriot
2007 CF30SK
dalemac377 is offline   Reply With Quote
Old 02-05-2013, 02:30 AM   #4
Full Time Camper
 
Join Date: Sep 2007
Location:
Posts: 1,415


If your in Fl. and have a 26 ft. tt you should be able to heat with a single 1500 watt electric heater. WE have a zf27rl and heat down to 15 degrees with 2 electric heaters. As far as the furnace. I would tape all joints in any flex hoses and check for leaks where ducks come through floor. Ther is a fan switch on thermostat you could see if its on low or high. I don't know if this just does ac or will do furnace also.
cwit is offline   Reply With Quote
Old 02-05-2013, 05:32 AM   #5
Full Time Camper
 
Join Date: Nov 2006
Location: Bradley, Il
Posts: 1,018


I believe the fan switch on the thermostat only controls the a/c fan speed. Furnace speed is fixed.
__________________
Dale & Carol
Bradley, Il
2007 F-250
2010 CF30SK Patriot
2007 CF30SK
dalemac377 is offline   Reply With Quote
Old 02-05-2013, 06:57 AM   #6
Full Time Camper
 
Join Date: Sep 2007
Location:
Posts: 1,415


I thought it might be but not sure. I never use mine.
cwit is offline   Reply With Quote
Old 02-05-2013, 10:12 PM   #7
New Camper
 
Join Date: Feb 2013
Location: Lutz, FL
Posts: 6


I have not checked the LP pressure. How does one go about that? Is there a gauge I can get to accomplish that check?
y2kvette is offline   Reply With Quote
Old 02-05-2013, 10:47 PM   #8
Site Team
 
Join Date: Dec 2007
Location: WI.
Posts: 9,153


Quote:
Originally Posted by y2kvette

I have not checked the LP pressure. How does one go about that? Is there a gauge I can get to accomplish that check?
Yes, there is a gauge for checking the LP pressure. I highly recommend that you contact either a service tech, or the local LP Co. you get your LP from to do this job for you.
But first, if I was you I would check to see if any of the furnace plates are off/missing/slightly ajar, etc.
If you don't have much air flow I would lean in that direction rather then LP pressure.
Low air volume is not an LP issue.

Edited by: Old Farmer
Lloyd is offline   Reply With Quote
Old 02-05-2013, 11:27 PM   #9
New Camper
 
Join Date: Feb 2013
Location: Lutz, FL
Posts: 6


Actually, I think there are 2 issues: air volume and heat quantity...and maybe a too small furnace.
The air volume I think I have solved to the best of the unit. The heat quantity is either LP pressure or burner related. So, I would like to check the LP pressure first as it is much easier than taking the unit apart to check the burner. What and where can I get a pressure tester?
y2kvette is offline   Reply With Quote
Old 02-06-2013, 04:12 AM   #10
Weekend Camper
 
Join Date: Apr 2012
Location:
Posts: 21
I am not certain of your tt layout but I have the 06 zinger 24' fb with the Atwood 8500 series furnace that sounds very similar to yours in most ways. First don't mess with the furnace gas regulator settings unless you don't want to sleep well. That being said I had my regulator adjusted shortly after puchase under warranty by a tech. If your gas hot water heater is igniting and stove working well than it sounds like gas pressure is not a problem. Start simple, the analog thermostatmay havea fan setting that allows for constant fan even when the furnace heat has discontinued. Mine also has a setting that shuts the fan off (and high and low) when it warms and turns-off the furnace or runs the blower all the time. The thermostat is not very accurate so rely ona seperate digital temp display like a weather station to determine actual temperature. A small electric space heater can get you a lot of heat for the buck compared to propane costs. I only use that when I'm awake though. I don't know if you might have freeze/condensation issues in Fla.I'm betting on the thermostat. Good luck,

__________________
2006 Zinger ZT-240-FB purchased 2011
uphaul is offline   Reply With Quote
Old 02-06-2013, 06:58 AM   #11
New Camper
 
Join Date: Feb 2013
Location: Lutz, FL
Posts: 6


I substituted a known good LP regulator with no change.
I think the air volume is normal after talking to Crossroads and Atwood.

The thermostat is working ok as I tested the heat with it at max ~90 degrees and the burner is running continuously.

At this point the only real concern is that there is very little heat coming out of the registers (and the exhaust).
Next I will take the unit out and apart to inspect the burner...and if necessary field test out of the trailer.
Otherwise, I may replace the unit with a 35K BTU Atwood or Suburban.

Only have 1-2 more months of needing furnace here in Florida, then will test the A/C for the rest of the year.
y2kvette is offline   Reply With Quote
Old 02-11-2013, 09:40 AM   #12
Full Time Camper
 
ewbldavis's Avatar
 
Join Date: Apr 2011
Location: Canton, OH
Posts: 937


Does trailer get warm? Our furnace "blows" softly from only 3 round vents, but heats well. I did tape off the bedroom vent to direct more towards rear of trailer (bedroom would be quite warm), but a wind tunnel this is not.
__________________
Eddy & Brenda
Canton, OH
2015 Silverado HD 6.0L
2014 Zinger 32QB
ewbldavis is offline   Reply With Quote
Old 02-11-2013, 09:47 AM   #13
New Camper
 
Join Date: Feb 2013
Location: Lutz, FL
Posts: 6


Last used outside temp go down to 35 degrees. The furnace ran all night and never got to 70 degrees on thermostat. I'm gonna pull unit and inspect the burner as it is not putting out very warm heat. thanks for your input.
y2kvette is offline   Reply With Quote
Old 02-13-2013, 12:27 PM   #14
Weekend Camper
 
manty's Avatar
 
Join Date: Feb 2011
Location: Minneapolis
Posts: 13
On our 2011 Zinger, the thermostat fan setting must be in "auto" (not "hi" or "low") to operate the furnace.
manty is offline   Reply With Quote
Old 03-04-2013, 09:15 AM   #15
Weekend Camper
 
Join Date: Sep 2012
Location: Mass
Posts: 12
We have a 2011 Zinger 29BH have camped one fall in NH 29F at night. The heater ran awesome. However, not considering the TT was new that year, we smoked up the TT we the oil that burned off. Sort of funny, we had all the windows open, still had plenty of heat! If you are getting low flow out the registers I would look at where the air is pulling from. You may here the motor running but is the wheel turning, or just riding the shaft? It may not be running at the correct speed.
Big Red is offline   Reply With Quote
Old 03-04-2013, 09:42 AM   #16
Full Time Camper
 
Join Date: Oct 2011
Location: Mn
Posts: 548
Have you check LP pressure at the heater or at the regulator.
Lebo

__________________
Lee & Jane and Black Lab Zoey
2008 Ford F250 CC Lariat 6.8L
2011 Crossroads Cruiser 31RK
Faribault MN
LeBo is offline   Reply With Quote
Old 03-06-2013, 09:54 AM   #17
Full Time Camper
 
ewbldavis's Avatar
 
Join Date: Apr 2011
Location: Canton, OH
Posts: 937


Good to inspect, but keep in mind 29 is cold camping.

We tend to use an electric portable heater just to supplement so we aren't burning propane like it is going out of style.
__________________
Eddy & Brenda
Canton, OH
2015 Silverado HD 6.0L
2014 Zinger 32QB
ewbldavis is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Crossroads RV or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 03:35 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×